  • Sep 11, 2011, 06:37 PM
    BrendaPate
    Correct amps for a timer
    Can a metal halide light that has to have a 20 amp circute to run on start up with a 15 apm timer
  • Sep 11, 2011, 06:43 PM
    lilpoppa
    It will start and run on your timer, but I can in no way suggest you do that. Your timer will be overloaded and be a fire hazzard. I strongly advise you get a timer with the proper amperage rating.
  • Sep 11, 2011, 06:43 PM
    ballengerb1
    If you mean the timer is only rated for 15 amps then the answer is no.
  • Sep 11, 2011, 06:45 PM
    donf
    It would depend on what the "inrush" current would be.

    Also, if the light truly requires a 20 amp circuit, then you need to remove the 15 amp timer because it may burn up on 20 amps.

    Normally, I would expect that the 20 amp circuit requirement is because there is an inrush current greater than 15 amps when the lamp is turned on. After the start-up, the current drops off.
  • Sep 12, 2011, 08:20 PM
    jerro
    What is the wattage of your metal halide light? A 400 watt metal halide light powered at 120volts only pulls 4 amps.