Upgrade my 100 amp panel to a 200 amp panel. I ran a #4 ground to the copper water pipe in the basement. The ground wire was accidentally cut. Can the ground wire be spliced?
![]() |
Upgrade my 100 amp panel to a 200 amp panel. I ran a #4 ground to the copper water pipe in the basement. The ground wire was accidentally cut. Can the ground wire be spliced?
Hi Brian and welcome, an expert will be along shortly, but in my area the ground wire must be continuous. Good luck
I see, KT or another expert will see this and answer your question. Good luck
This grounding electrode conductor either neds to be a continuous conductor, or can be spliced with an irreversible connection, which would be a compression connection.
You can find a butt splice connector at an electrical distributor, would need to borrow or rent a crimping tool.
Some distributors rent out these tools.