  • Aug 29, 2011, 11:10 AM
    Brian75
    #4 Grounding wire 200 amp service spliced?
    Upgrade my 100 amp panel to a 200 amp panel. I ran a #4 ground to the copper water pipe in the basement. The ground wire was accidentally cut. Can the ground wire be spliced?
  • Aug 29, 2011, 12:38 PM
    parttime
    Hi Brian and welcome, an expert will be along shortly, but in my area the ground wire must be continuous. Good luck
  • Aug 29, 2011, 03:41 PM
    Brian75
    Quote:

    Originally Posted by parttime View Post
    Hi Brian and welcome, an expert will be along shortly, but in my area the ground wire must be continous. good luck

    Thank you parttime

    It has already been inspected. I know code here is that it must be continuous too. Didn't want to replace it if I don't have to about $100 to replace.
  • Aug 29, 2011, 04:28 PM
    parttime
    I see, KT or another expert will see this and answer your question. Good luck
  • Aug 30, 2011, 07:41 AM
    tkrussell
    This grounding electrode conductor either neds to be a continuous conductor, or can be spliced with an irreversible connection, which would be a compression connection.

    You can find a butt splice connector at an electrical distributor, would need to borrow or rent a crimping tool.

    Some distributors rent out these tools.