Issue with one of the two service lines into the house
I live in a old house, built in 1867, and have a 100-AMP main breaker that was put in in 1978. Recently I have had an issue with the electricity. One of the two service lines coming into the house will read 10-volts with my multi-meter when the main BUSE fuses are in, but when the fuses are removed the service line reads 120-volts. I have tried shutting off every breaker in the box, one by one, to see which breaker hold the issue, but none of them make the multi-meter read 120-volts. Amazingly enough, the only thing that seems to make the voltage jump back up to 12-volts is when the pump for the well turns on. I did check the connections there, and found the ground wire was carrying the volts and fixed that issue, but was still wondering if there were any other reasons for the low voltage reading. I am not an electrician but I am a willing DIYer.