    Bryant 395CAV Furnace Won't Start
    The furnace typically takes three or four ignition cycles before flame extends down burner to reach the flame sensor. It seems to light only halfway down burner on most attempts. Sometimes reaches shut off and then I have to flick switch to repeat cycle. Help.
  • Jan 31, 2007, 04:46 PM
    NorthernHeat
    If I understand you correctly, all the burners need pulled and cleaned. Sometimes rust or a spiders web gets in the little crevice at the end of the burners keeping it from extending the flame to the next burner.
  • Jan 31, 2007, 04:52 PM
    jeffc
    Thanks. Will give it a try.
  • Jan 31, 2007, 06:38 PM
    jeffc
    Quote:

    Originally Posted by jeffc
    The furnace typically takes three or four ignition cycles before flame extends down burner to reach the flame sensor. It seems to light only halfway down burner on most attempts. Sometimes reaches shut off and then I have to flick switch to repeat cycle. Help.

    Works like a charm. Thanks again.