What derating should be used for NM-B in insulated ceiling?
I am building a workshop in central North Carolina. It is 1 1/2 story with the second floor unconditioned space. The ceiling joists are 2x10 with R30 fiberglass insulation. What derating, if any, do I need to use for NM-B cable runs in the ceiling?
The runs will either run lengthwise with the joists or crosswise to the joists through holes drilled about 3 inches from the bottom of the joist (ie about 1/3 of the way into the 10" of insulation).
The building is in a shaded area, but being in NC, worst case temps in the second story might reach 115 degrees (46C). Can I use a gradient between the conditioned space and the unconditioned space (46-25=21C, 21/3=7C, 25C+7=32C) and use the 31-35C derating factor??
Thanks in advance,
Tom