Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   AC Compressor on, Inside air doesn't work, heat works (https://www.askmehelpdesk.com/showthread.php?t=578427)

  • May 26, 2011, 03:25 PM
    floyd4467
    AC Compressor on, Inside air doesn't work, heat works
    Ugh, Every season, when I switch from heat to air, neither one works. I've had repair men replace pratically everything. Now it's AC time again, outside compressor is on, inside is not. Switched to heat & that comes on, so it's not the fan. I have new batteries in thermostat, usually it will kick on eventually, hopefully before the compressor freezes up. Any suggestions? It's a Goodman GMP-075-3-Rev. P.S. I've had the fan motor replaced, mother board, etc
  • May 27, 2011, 06:51 PM
    T-Top
    The blower should come on the same time the A/C kicks in. (rule of thumb if a time delay is not used). Can you turn the blower on from the thermostat if you switch the fan to ON? If no, you may have a bad thermostat or blower relay bad for cooling. Some systems use 2 speed blowers 1 for heating and 1 for cooling, if a relay goes bad you may have blower action in one mode but not the other.