  • Jan 26, 2007, 06:53 AM
    Ohio_Remodeler
    1 Attachment(s)
    Retail Storefront Circuits
    A 12/3 homerun supplies circuits R21 and R22. These 2 circuits supply a storefront. R21 supplies 3 receptacles controlled by a switch. R22 also supplies 3 receptacles controlled by a switch. They only supply the receptacles shown. 600.5(A) states "Outlets must be supplied by a branch circuit rated 20 amps or more and that supplies no other load."

    1. Is there any code issue with sharing a neutral to supply these 2 storefront circuits?

    2. Are there any other flaws in this storefront plan?
  • Jan 26, 2007, 04:09 PM
    tkrussell
    Your reading the wrong section for show windows, look at 210.62 and 220.3(7).

    Your seem to have enough circuits and quantity of outlets, but I don't know the length.

    Multiwire circuits is fine.