  • May 5, 2011, 07:21 PM
    butters_30
    AC Won't Shut Off
    I have a RHT2300B Honeywell Thermostat and my AC won't shut off when it reaches desired temp. It will be 72 and I will set it to 71. It keeps running and it will be 69 and it won't shut off. Seems uncommon. My wiring in the thermstat is the Red into R, Green into G, White into W, and Light Blue into Y. The only other terminal is the O/B and I no that's not supposed to be used. Before I had a White Rodgers thermstat that came equipped with a different wiring panel that had a Rh/RC jumper wire and I never had any problems with my AC or heat not cycling or turning off. Any help or feedback is greatly appreciated.
  • May 6, 2011, 10:25 AM
    Seann
    Hi

    As you mentioned , used terminals are R,W,Y,G
    In this R is power,W is heating ,G is fan and Y is compressor
    In RTH2300B when you run Ur cooling,do you see word cool on on display,if cool on is there then that means the set point has still not been satisfied.
    If cool on is not there,then you may try these steps
    1) put your system switch to off fan to auto
    If compressor is still running
    Then remove face plate off the wall
    If compressor is still running then remove Y wire out
    If compressor still running then its your compressor for sure
    But , if your compressor stops as you put stat off the wall
    Then remove Y and G wire out
    Put G to Y,leave Y wire unconnected
    Put stat cover back on wall
    Put your system to cool fan to auto
    If fan starts running ,then it's the stat
    But if stat behaves normal,fan comes on and off as you call and end the call for cool
    Then its your compressor

    Try this
    If still cannot figure out
    Call Honeywell Tech Support.
  • May 8, 2011, 09:44 AM
    paultg
    Check to see if your contactor in the ac unit is stuck