    Heater popoff valve
    What causes a waterheater popoff valve to leak I've replaced 4 this year
  • May 5, 2011, 03:42 AM
    afaroo
    1 Attachment(s)

    Are you talking about The T&P Valve see the image below?

    If that is what you mean then you need to find the cause why it pops.

    In normal operation of the T&P valve, no water should be discharged from the valve.

    A T&P valve that discharges is an indication of an abnormal condition.The causes of discharge can be thermal expansion, excess system pressure, low temperature relief (T&P) failure, too high temperature setting, or something in the water heater causing excess temperatures.

    You need to check the water Temperature and the water pressure, and let us know, Thanks.

    John
  • May 5, 2011, 06:10 AM
    ma0641
    If this has happened with the frequency you say, check the water pressure at your HW heater with a Watts test gauge. It should not exceed 75#. There was a post last week with a same question and he found 125#. If your water line is equipped with a backflow checkvalve and you do not have an expansion tank, you may also be overpressuring the system that way or you may have a bad main pressure control valve.