T&P valve replaced after occasional discharge - new one also discharging.
The new TPR valve is discharging occasional water too. I am getting about a half gallon a day discharge.
It is not a temperature issue from what I have researched because I have kept the temperature on low.
A little history: I moved into the house recently. Saw water coming from the valve onto the floor of the garage and found out about replacing the TPR valve which I did so a few days ago.
I now am going to get a pressure gauge (Watts DP IWTG) at Home Depot and see what the highest reading is.
My main concern is that there is a danger here to be aware of. If the Temperature and Pressure relief valve is working by discharging, is there still any immediate danger to be aware of?
I have also read up on expansion tanks. Would they suddenly be something that is needed or maybe it was needed all along by the previous owner but they ignored this water discharge.
Any and all help will be appreicated!
Thanks!
Phil
Comment on argaiu1017's post
Hello,
It turns out that my water pressure into the house was 140psi - yikes!
I got a new pressure regulator installed by a plumber. Now all is fine with the water heater.
Thanks for all the responses!