    tazer
    Lennox g26 series problems?
    Circulating fan runs constant won't shut off. Thermostat shut off. Replaced blower motor circuit board, still runs all the time. What now
  • Apr 24, 2011, 02:53 PM
    KC13

    Does the system work in the heating mode? Many units with electronic control are designed to run the blower continuously in the event of an open temperature limit device.
  • Apr 24, 2011, 08:20 PM
    tazer
    Comment on KC13's post
    No, the system does not work in the heating mode. I did as it turns out have an open limit switch. It tripped because of a defective combustion fan that I now have to replace,