Federal Pioneer Stab-Lok BE 132-64 200Amps 120/240V 1 phase 3 wires
	
	
		I have a Federal Pioneer Stab-Lok BE 132-64 200Amps 120/240V 1 phase 3 wires circuit breaker panel with a 30AMP circuit breaker hooked up to an existing electric cooktop.
Existing electric cooktop is a Jenn-Air CCS446-C cooktop with the ratings 7,000W at 240V / 208V.
Need to hook up a BOSCH NET5054UC cooktop to it - it is rated at 7,700W at 240V  /208V.
Have I exceeded the limit of the 30Amp circuit breaker?
	 
	
	
	
		Comment on tkrussell's post
	
	
		I understood the math... (long story with my education there)
I am in an apartment and everyone is telling me that it is 208 volts - I have a voltmeter but cannot find a spot on the circuit to measure - where can I measure?
The original unit (Jenn-Air) is rated at 5,300 watts at 208 volts.  Which means 25.48Amps.  If the voltage change, the wattage should change too - you may be incorrect in dividing 7k watts into 208 volts.
For the BOSC NET 5054UC installation instructions: -
See page 9 of the first document here: https://portal.bsh-partner.com/TCcustomBSH/controller/download_file?PDFOBID=tgslirkcdcso0pdmdb---j4p&UMOBID=tgsliqecdcso0pdmdb---j4p
I can't seemed to find the other cooktop's specs except to include a picture here: https://picasaweb.google.com/ting.roger/JennAirCCS446C?authkey=Gv1sRgCNO9tcftnumYQg&feat=d  irectlink
	 
	
	
	
		Comment on tkrussell's post
	
	
		Appreciates all the comments so far!