-   -   Sears 600 furnace blower will not cycle (https://www.askmehelpdesk.com/showthread.php?t=568433)

  • Apr 6, 2011, 11:59 AM
    kidd7
    Sears 600 furnace blower will not cycle
    I have a Sears 600 furnace; the burner cycles normally, but the blower is constantly on. There is a summer / auto switch that will basically turn off the furnace when on summer; no cycling at all. Any Ideas? Thanks.
  • Apr 30, 2011, 11:22 AM
    Kyle_in_rure
    Might have a loose wire at your thermostat. Make sure all the thermostat wires are secure at the thermostat and where they connect at the unit. Hope this helped.
  • Apr 30, 2011, 07:05 PM
    KC13
    2 Attachment(s)
    If the unit is equipped with a combination fan/limit control, it may be stuck in the "ON" position. If so, try gently rotating the dial counter-clockwise to see if the fan shuts off.