As I mentioned there is no ground wire. I guess that's the way they were wired. The house has vaulted ceilings, so the previous owner had some one run conduit from the panel to the roof and then drill through the beam that runs in the middle of the ceiling. So conduit goes from the panel to a box on the roof and then down into each room. There is a hot wire and a neutral wire only. There is no ground wire at all. So I took a volt meter and ohmed out the hot wire, touching the hot wire and also the metal fan box. I got 68volts instead of the 120volts. Then I touched the neutral wire and also the fan box and got 38 volts. I figured maybe it was coming from the source. So I traced it back to the panel and found the breaker it was on. I disconnected the wire that leads to the ceiling fans. Left the breaker on and got 120 volts out of the breaker. When I touched the neutrual buss in the panel I got 0 volts. Like I mentioned there is 6 different ceiling fans on this 15 amp circuit.
Comment on Stratmando's post
My problem is the ceiling fans are running so slow that its pointless to have them on. But there's a ceiling fan in the kitchen that is not on the same circuit. This fan runs on 120 volts. It runs fast or normal I should say. This is why I am writing this. I noticed the bed room fans run so slow and the air output is so minimal that its pointless to have them on. Could I be getting a low voltage due to to many fans on a circuit and voltage through a neutral due to a lack of a ground wire from the panel ?
Comment on Missouri Bound's post
They are controlled by the pull chain. No they don't come on all and once
Comment on Missouri Bound's post
Yea that's the voltage I came up with on the first fan. What's weird is when I disconted the wire at the breaker and ohmed the breaker. I get 120volts. I touch the neutral buss in the panel. I get 0 volts. But at the first fan I get 68 volts out of the hot leg and 38 out of the neutral. Its only a distance of 30 feet. The panel is in the garage. The farthest fan is about 110feet away. All the other fans are are in the 60 range on the hot leg and in the 30 range on the neutrals. I thought maybe not having a ground wire in the circuit might be causing voltage through the neutrals.