  • Mar 22, 2011, 08:26 PM
    shylipps
    Why only 120 V at the breaker box to A/C ?
    Thought there should be 240V kind of checked main breaker at power pole and read 120V from breaker to ground but 240 from breaker to bus.
  • Apr 17, 2011, 08:08 PM
    KC13
    Is the breaker installed correctly? I ask because I encountered this very thing on a service call last week. The standard double-pole breaker had been replaced with a slimline, and was positioned such that it was connected to the same line on both poles. Moving it one space corrected the problem.