Pressure testing gas line
I am installing a new LP gas line into my basement. I have the line run and have a pressure tester connected to the line. I am getting conflicting info on the pressure and time I need to test to. I found an old thread (Aug 2005) on this forum that said 10 psi for 15 minutes. I also found a City of Berkeley document that said the same thing.
I have 2 friends that works doing HVAC installations for separate companies. One tells me 60 psi for an hour, the other tells me 40 psi. My gauge only goes to 20 psi. I tested it at 28 psi for an hour and had less than 1/4 psi drop. Overnight, it dropped about 2 psi.
Do I have a problem? I have tested all connections with soapy water and see no bubble.
Thanks,
Glenn