Ducane Furnace - No power to fan motor
I have a Ducane DOLA84/95F4-AB Oil Furnace/air handler. The AC system is hooked into the same unit. The furnace fires up and makes heat with no problem. However the fan is not spinning.
First I pulled the fan and bench tested it - ran it on each speed for a while under load and everything seemed fine.
Checked power to the fan and found that it was not receiving any. I then followed the lines back to the circuit board and the lines running to the fan were not receiving power from the circuit board.
After pulling the circuit board I found the K1 Relay to be burnt on the back of the board as well as resistor R5 and R6.
If anyone has any information concerning this problem I would greatly appreciate it.
Thanks!
Comment on mygirlsdad77's post
Thanks mygirlsdad77... Like I said I ran the motor on the bench for a while and everything seemed all right to me, but I'm not a pro.
Is there a separate way to check the capacitor to make sure that's OK? Also, do you have any idea what could have made the board blow? Is this a fairly common problem? I just don't want to replace it and run into the same issue. Is it possible that too much resistance on the fan caused it. I know I don't have the best air return system set up right now because of some temporary construction. Thanks again!