Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Can I use 8 2 wire with a double pole breaker if so how? (https://www.askmehelpdesk.com/showthread.php?t=557323)

  • Feb 23, 2011, 06:04 PM
    sans369
    Can I use 8 2 wire with a double pole breaker if so how?
  • Feb 23, 2011, 06:15 PM
    stanfortyman

    How about some more detail?

    What are you wiring?
    What is the draw?
    Why #8?

    What exactly do you mean by "how"?
  • Feb 23, 2011, 07:38 PM
    sans369
    Stan,
    Thank you for takeing the time to answer my question.
    I am wiring a cooktop that is either 208 or 240 volts. Electrcian ran wire but is gone long story. Am homeowner with my carpenter who has done wiring in the past. Am confused because always thought you needed three wire for 220. Was told you can use white wire as second leg rather than as neutral. Is that corect?
  • Feb 23, 2011, 09:12 PM
    ma0641
    If the cooktop is straight 240V you don't have a neutral, black and white are conductors. Retask the white through the breaker and mark it with black tape. If the cooktop is 120/240 you will need a 3 conductor with a neutral.