Power requirements using a 112.5 kva transformer
![]() |
Power requirements using a 112.5 kva transformer
The total volt-amps are the same on the primary and secondary. If the secondary is at 480V, 150A, that's a total of 72 kVA.
Therefore, if the primary is at a voltage of 208V, the current must be 72,000/208 or about 350 Amps.
I will assume this is 3 phase, in which case the calculation is for example;
480 Volts x 150 Amps x 1.73 = 124,560 VA