    Grounding new outlets when house has old two wire no ground
  • Jan 30, 2011, 04:12 PM
    ma0641
    What type of wiring is in the house? How old? Some older BX wiring used the conduit as ground. Old Knob abd Tube may or may not have a ground wireCheck for a ground by testing for voltage between the black wire and the box. If you get 120V you have a ground and could use a ground clip on the box.. If you are sure there is no ground, you need to run a separate ground wire, perhaps to a grounded water pipe running in the house.
  • Jan 30, 2011, 04:56 PM
    hkstroud

    Outlets cannot be grounded if you have no ground wire.

    You can replace ungrounded outlets with grounded type outlets by replacing the first outlet in the circuit with GFI outlet, feed the remaining outlets through the GFI, replace the remaining outlets with regular grounded type outlets and mark them "ungrounded".
  • Jan 30, 2011, 05:00 PM
    stanfortyman
    Quote:

    Originally Posted by ma0641 View Post
    Old Knob abd Tube may or may not have a ground wire

    I've never known K&T to have a ground.


    Quote:

    Originally Posted by ma0641 View Post
    Check for a ground by testing for voltage between the black wire and the box. If you get 120V you have a ground and could use a ground clip on the box..

    Only partially accurate. Even if a ground reading is found it may mot be a safe ground to use.
    If armored cable was used it must have a bonding strip inside the sheathing. Old BX/AC cable without this strip is not legal or safe to use as an equipment ground.


    Quote:

    Originally Posted by ma0641 View Post
    If you are sure there is no ground, you need to run a separate ground wire, perhaps to a grounded water pipe running in the house.

    Using a water pipe is a last resort, and only allowable if certain specific are met. Safe to say this is not a good idea.

    Running a new cable is always the best bet.
  • Jan 30, 2011, 07:36 PM
    Barndoor
    Hey Guys, The house was built in 1950 it has wiring that looks like a dark black woven material.
  • Jan 30, 2011, 08:02 PM
    hkstroud

    Old style non metallic cable. Probably doesn't have ground wire but look closely. I've seen it with a ground wire and used with ungrounded outlets. The electrician just connected ground to the box or just folded it back up into the cable clamp.
  • Jan 31, 2011, 06:18 AM
    Barndoor
    Thanks a lot you all have been very helpful. Barndoor