-   -   Occasinal tpr relief valve leaking? (https://www.askmehelpdesk.com/showthread.php?t=548193)

  • Jan 26, 2011, 06:40 PM
    Schoma
    Occasinal tpr relief valve leaking?
    Tpr valve occasional drips water. I have a well
  • Jan 26, 2011, 07:05 PM
    hkstroud

    What is well pump pressure setting? Do you have a check valve between well tank and house?
  • Jan 26, 2011, 09:22 PM
    ma0641
    There are only two reasons for a discharge. They are overtemp and overpressure. When TPR valves age, the spring weakens and they will open below the set pressure. Check temp 125+/-and water pressure 40-60psig and if they are in line, change the TPR.
  • Jan 27, 2011, 07:17 AM
    massplumber2008
    1 Attachment(s)

    HI guys...

    Brian, there is another reason... called a CLOSED SYSTEM where backflow preventers, pressure regulating valves and check valves create a closed system that won't allow for the expansion that a water heater creates on water and will usually relieve the excess pressure by relieveing it through the T&P valve.

    The answer in these "closed system" setups is to install an EXPANSION TANK in the cold water supply... see image.

    With that being said, I can't be sure this is the issue for SCHOMA as we need to know if there are check valves or other valves I mentioned above in place in his system.

    At a minimum, I would definitely replace the T&P valve, for sure!

    Will check back later!

    Mark
  • Jan 27, 2011, 03:06 PM
    ma0641
    Comment on massplumber2008's post
    Good call, Didn't think about that since I rarely see one without an expansion tank.