Nordyne furnace: no voltage to pressure switch
Hi Folks,
My furnace inducer blower goes on and stays on without igniting the furnace.
The thermostat will not turn off the furnace, I need to physically switch it off.
Brand: Nordyne
Model: L1RA 090N 16B
The circuit board does emit a single red led flash every few seconds:
In the manual this indicates:
Limit Circuit Open or External Load On "W"
So I began some testing:
- continuity tests on the two flame rollout switches were successful while the furnace was off
- voltage tests were successful when furnace was on and they are both closed (around 24 volts on both sides of the posts, while the furnace was running)
- continuity test on the Pressure Swtich shows continuity when I manually (with my mouth) suck the pressure out of the tube
- continuity test fails on Pressure Switch when I blow into the tube
- voltage test FAILS on the Pressure Switch when the furnace is running, no voltage on either post
- I jumped the two pressure switch wires, eliminating the switch and no change, furnace does not ignite, 1 single flash on the LED.
- I removed the pressure switch and did a voltage test directly on the two orange wires going into the pressure switch, this show 0 volts on both wires.
So... my questions:
- what does "Load on W" mean? Is this the W wire from the thermostat?
- no voltage is going to the blower switch, does this sound like circuit board could need replacing?
- what else should I look at?
This issue first popped up 4 days ago...
After jumping the limit switches and doing some tests, banging some things around and some cussing, a and beer the furnace began functioning properly.
It worked fine for the next 3 days, cycling on and off as expected with the thermostat.
Last night it reverting to its bad behavior and I can not figure it out...
Why am I not getting power to the pressure switch?
Thanks in advance folks