Originally Posted by Lazarwulf
Short summary. If the switch at the Payne gas furnace (from 50's) is on, the blower stays on. Gas seems to light properly with the thermostat. I have replaced both the fan limit control and the limit control (both made by camstat). There are no relays.
This is a definate fixer-upper house, and I have seen some strange things. I am convinced that the wiring is completely wrong. To make matters worse. All wires are black with the exception of the 120v wires coming into the furnace and the blower motor wires.
A summary of how this should be wired would be most helpful.
Instructions like connect the 2 leads from the transformer out to the...?
Connect the >>?
List of wires.
I of course have 120v in to the furnace.
120v single pole switch.
24v transformer with 2 wires (both black).
2 thermostat wires.
2 lead Camstat FAL7C 20BT-120-AB fan switch.
2 lead Camstat L59-7B-A limit switch.
2 wire pilot.
2 wire gas switch.
Blower motor with 2 wires (black and a white).
Currently this is how it is wired.
120v black -> 120v single pole switch and
120v white -> blower white and transformer out
120v single pole switch -> black 120v and black blower wire
Thermostat wires -> 1 to transformer nut and 1 to gas switch
Gas switch -> 1 to transformer nut and 1 to pilot
pilot -> 1 to gas and 1 to transformer
transformer out -> 1 to 120v white and 1 to Camstat L59-7B-A limit switch C. (right side)
Camstat L59-7B-A limit switch -> 1 to transformer out and 1 to black blower
Camstat FAL7C 20BT-120-AB fan switch -> 1 to 120v black and 1 to black blower
Blower motor -> black connects to single pole switch, Camstat FAL7C 20BT-120-AB, and Camstat L59-7B-A
All this wiring except the obvious exceptions is in a "junction box" built into the furnace.
Damn that took a while to write out :)
-Twain