Trane XR80 furnace blows cold air continuously.
This is a 6 to 8 year old (I believe) propane, forced hot air, horizontal, updraft unit. It is in a presently unoccupied apartment, but I would like to repair it so the apartment pipes don't freeze. So far I replaced the ignitor about two weeks ago and thought all was well. I noticed about a week ago that the circulation fan was running continuously, but couldn't get to check until today. I found that the diagnostic light was blinking 9 times which the chart says "Check Ignitor". I also found that the flame sensor wire was charred for the 2 inches before it conects to the sensor. I repaired that wire by cutting off the cahrred section and put on a new connector. I have contiuity from the sensor to the board. I also cleaned the sensor. I tried removing the recently replaced ignitor, it had a white, ashy appearance, cleaning the surface, and reinstalled. It does not glow when initialized. I measured 2.5 volts at the ignitor conector. I tried cleaning and installing the previously replaced ignitor, but no joy. I intend to get new ignitor and flame sensor on Monday but it's quite a drive to the supplier and if I need to get a control board, I'll bite the bullet. Thanks for any help or guidance that you can give,
Tony AKA Antiqueynot