    what gauge wire to use??
    I need to install wiring for a whirlpool induction cooktop model gci3061x but don't know what gauge wire to use. The booklet that came with it doesn't say.
  • Jan 12, 2011, 03:59 PM
    stanfortyman

    What is the wattage of the unit? It will probably say in kW.
  • Jan 12, 2011, 04:02 PM
    stanfortyman

    I got it right from their web site.
    Quote:

    Electrical Requirements
    40 Amps. 60 Hz. 240 V.
    You can use 8/2NM cable on a two-pole 40A breaker.
  • Jan 12, 2011, 04:03 PM
    stanfortyman

    Are you prepared/experienced enough to install this circuit, or are you having someone do it?
  • Jan 12, 2011, 04:26 PM
    lawdeedah
    Yes I am experienced enough to install it. Thanks to the person who gave me the right wire to use!