  • Jan 8, 2011, 06:02 PM
    timotao
    Barn Electrical
    Barn electrical, The price of copper is to expensive so can I use 4/0 4/0 2/0 urd to run between the main disconnect at the meeter over 180 feet to the 200 amp main breaker panel? And then run a separate ground wire in the conduit with it?
  • Jan 8, 2011, 06:12 PM
    stanfortyman

    Yes you can.
  • Jan 9, 2011, 05:39 AM
    tkrussell
    As Stan said, yes, but why not 4 wire URD? Unless you already have 3 wire and want to use it up.