"How far is this main line from your electrical service entrance?" I just bought this house and I'm waiting until escrow is done. This problem was found by the home inspector. See photos
Comment on jcaron2's post
The main supply line is above the service panel about 1 foot away with clamp on water line.
Comment on tkrussell's post
See YouTube video just 2 photos in it. I switch from private to public so you should be able to watch video. Just give a few minutes for YouTube to reset privacy settings.
Comment on jcaron2's post
Or maybe it's just a #6 clamp with no wire actually connected. If so, it's a really easy fix! :-)
Comment on jcaron2's post
Grounding 13. SERVICE / REPAIR: Grounding is in question. Although clamp is connected to copper supply line that line is connected to a "plastic" service line. Additionally there is no bonding wire at the water heater. Recommend an electrician.
Comment on jcaron2's post
Also, inspector said that he could not find a grounding rod.
Comment on jcaron2's post
Ok I wait until escrow done and I will remove panel and see if ground is there. Thanks!
Comment on jcaron2's post
Woops... that last "paragraph" was supposed to get deleted. It's really annoying that you can no longer edit your posts on this site.