    Microwave/Oven Combo 40 amp rough in whire size
    I am installing a new Whirlpool microwave/oven combo (model GMC275) which calls for a 40 amp circuit. I need to run a new home run to the sub-panel and install a 40 amp breaker. The run is about 60 feet. What is the romex wire size I need to use?
  • Jan 10, 2007, 08:13 PM
    tkrussell
    #8-3 with ground, copper NM-B Romex