    marykrhodes
    Can the oven outlet can be used for a dryer also?
    Hello,
    I just moved into an older home and there is a stove plugged into an outlet that I have always associated with a dryer. How do I find out if the dryer can run from this outlet?
  • Dec 23, 2010, 02:50 AM
    joypulv
    A large single 220 volt outlet for a large plug is OK to use for a dryer or a stove.
    It helps to learn your fuse box or circuit breaker box, even if you are renting, and to draw a diagram. That circuit will be 30 amps.
  • Dec 23, 2010, 02:59 AM
    joypulv
    Wait - older home... the 220 line could be 3 wire when you need 4 wire. You either need to test it with a multimeter or hire someone.
  • Dec 23, 2010, 05:01 AM
    stanfortyman
    Quote:

    Originally Posted by joypulv View Post
    A large single 220 volt outlet for a large plug is OK to use for a dryer or a stove.
    It helps to learn your fuse box or circuit breaker box, even if you are renting, and to draw a diagram. That circuit will be 30 amps.

    Sorry, this is not at all accurate.

    A "large single 220 volt outlet", is absoutely NOT the same for a range and dryer.

    First off, these circuits are 120/240v. They have two hots and a NEUTRAL.

    Older codes allowed the omission of the ground wire and the equipment ground of the appliance was bonded internally to the neutral terminal.
    This is what is generically called a 3-wire range or dryer circuit.

    Newer codes do require a dedicated grounding conductor and 4-wire receptacles.

    A range is typically a 40 or 50A circuit with a 50A receptacle.

    A dryer is a 30A circuit with a 30A receptacle.

    Generally the instructions with a dryer will be clear in that it should be connected to a 30A circuit.
  • Jan 1, 2011, 11:15 AM
    joypulv
    Comment on stanfortyman's post
    Sorry for the mistake
  • Jan 1, 2011, 12:01 PM
    donf

    Please note that the NEC requires that the range and dryer be on their own dedicated circuits. They cannot share the same circuit.