Draft Inducer motor (Bryant 373LAV hoz) issues
I trigger the furnace using the TEST lead to the common lead. The inducer motor starts (somewhat slowly), the ignitor glows, missing gas flow rom the GSV and then the blower tuns on and then shuts off. No fault code. I replaced the gas valve, no change. I checked the pressure switch for the draft inducer motor and that appears to be good when I suck into it through the tubing, the swicth opens and closes, I measured with multimeter for resistance. In circuit the switch will not close, I don't read 24 VAC from any terminal lead to grnd. Is it the inducer motor because it is not providing enough back pressure? Help. The inducer motor squeels upon start up, appears slow.
Checking the volatges on the terminal boardi need to know what the volatges are during operation. I get for voltage at G is 24 VAC, Y .1 VAC, W .1 VAC, and R .1 VAC. Are these normal? Possible computer problem also?
When I check the voltage to the gas valve I read 0 VAC in testing mode, there's no clicking of the solenoid or is it enerigizing . When I disconnect the lead from the GSV valve I read 14-15 VAC on the lead from the computer. No load?
Does the computer inhibit the 24 VAC signal to the GSV since the pressure switch on the draft inducer motor does not close? I'm about to change the inducer motor, any suggestions or recommednations, thanks for your time, much appriciated.