  • Nov 29, 2010, 10:04 AM
    tomcat1894
    Bare Copper Ground conductor
    Are you allowed to run bare copper ground conductor into a plastic gang box (20 amp bathroom circuit)?
  • Nov 29, 2010, 10:43 AM
    donf

    Yes, but do not attach the conductors to the box. Connect the device grounds together, first, and then push them into the box first. Next do the Neutral conductors and finally the hot conductors.
  • Nov 29, 2010, 12:11 PM
    tkrussell
    Just to be clear, the bare ground must be part of a cable or conduit, not run alone.
  • Nov 29, 2010, 03:04 PM
    stanfortyman
    Quote:

    Originally Posted by tomcat1894 View Post
    Are you allowed to run bare copper ground conductor into a plastic gang box (20 amp bathroom circuit)?

    Why are you asking this? There has to be more to the story.

    Can you give us some details about what it is you are trying to do?