    Replacing old subpanel
    I am replacing an old subpanel with a new 125 panel (main breaker in place). The old sub-panel was fed by a 50 amp breaker on the main panel. It appears to only have one hot (the white) and a neutral ground (the bare) coming in. When I try to wire white and black to main breaker, and ground (bare) to ground bar, I only get half the slots. Am I basically getting 120 coming from the 50 amp breaker in the main?
  • Nov 29, 2010, 05:46 AM
    tkrussell

    Sounds like the 50 amp circuit is only 120 volts. You should have tested these wires before beginning work, and see how they are connectec at the source.