What size ground do I need for a 100AMP sub panel 300ft away?
I'm installing a 100A sub-panel 300ft away from the main breaker. I plan on using #1 AWG copper wire for both the 2 hots and neutral to accommodate Vdrop for up to 70 solar PV micro inverters that I am using. What size ground should I use? Not accounting for distance I know I can use #8 AWG copper. Does distance/Vdrop matter for the ground? What size ground do I need for a 100AMP sub panel 300ft away?
The design will be:
1. 100A breaker in MAIN
2. 100A Outdoor Circuit Breaker enclosure acting as service disconnect next to Meter
3. 100A Sub-panel with 6 double-pole 15A breakers 300ft away
4. Max AMPs for all inverters would be (.8A per inverter X 70 inverters/solar panels) * 1.25 = 70A
More specifically, I would like to know what the "minimum" size ground wire is in this scenario and also discuss any "recommended" size as well and any reasons for the sizing.
Note, I am familiar with non-bonding neutral and ground and using a grounding rod out by the sub-panel.
Thanks!