  • Nov 11, 2010, 10:43 AM
    jtscat73
    Neon transformer with GFI
    I am replacing a failed 6kv neon transformer. The new one has no voltage out but has
    A secondary ground fault connection. Must this be connected before you get output, if so, where?
  • Nov 12, 2010, 07:32 AM
    tkrussell
    If you can provide the make and model number of the neon transformer, we may be able to find the datasheet on this.
  • Nov 12, 2010, 09:14 AM
    jtscat73
    [QUOTE=jtscat73;2598175]I am replacing a failed 6kv neon transformer. The new one has no voltage out but has
    A secondary ground fault connection. Must this be connected before you get output, if so, where? Model #HM106ND protection requirements in UL2161 UL listed 3HWK E307554
  • Nov 12, 2010, 12:01 PM
    tkrussell
    You gave no make, so did a search for the model number. Is this your unit?

    6.5KV UL Neon Power Supply Transformer - Detailed info for 6.5KV UL Neon Power Supply Transformer,power transformer,6.5KV UL Neon Power Supply Transformer,HM106ND on Alibaba.com

    Not much for specs there.

    So what is the issue?

    What does a secondary fault connection mean?

    The secondary has a ground fault with no load?

    Transformers or ballasts often have fault currents, and do not work well on GFI devices.