  • Nov 10, 2010, 12:32 PM
    billtvt
    Problem installing Tstat -HONEYWELL T8601D
    I purchased the above referenced Programmable tstat to replace a different brand. My system is pretty simple, just a hot water heater for a radiant floor, no cooling or fans. I thought it would be straightforward- just connect red to red, white to white, and jumper if need be. I can't however, get it to work correctly. I suspect I am not jumping the right terminals together, but the user manual for the Honeywell is not real user friendly. See the attached diagram for my old tstat- which was working fine. Hopefully that will shed enough light on it for someone to help me with the proper wiring for the Honeywell. Any help is much appreciated.

    Thanks
  • Nov 10, 2010, 07:29 PM
    Joshdta

    Red to r
    White to w
    Did you do the installer setup correctly
  • Nov 11, 2010, 05:02 AM
    billtvt
    That is the setup I tried first - seemed obvious but nothing came on. So then I tried jumping the r and c terminals, because the old tstat had a jumper between the r and the rc terminals. That didn't work either. I then jumped the white to the c terminal, and the tstat turned on, however every time it called for heat it would click off for a couple of seconds and turn back on. So, something is apparently backwards or incorrect.
  • Nov 11, 2010, 05:52 AM
    Joshdta

    If you jumped form r to c you may have burt up a transformer or a fuse