    Do I need to change my circuit breaker?
    Thanks for your reply. I purchased a PTAC unit and nowhere in the owner's manual does it indicate amps required; however, on the plug it has 20Amps so I'm assuming that what it requires. My question is that the circuit breaker is 30 amps, do I need to change it to 20 amps or is the 30amp breaker okay?
  • Nov 1, 2010, 04:17 PM
    stanfortyman

    How about telling us the make and model?

    What do the instructions/manual say? They would indicate the required circuit amperage.
  • Nov 1, 2010, 04:46 PM
    ballengerb1

    Please describe the plug on your AC unit. If it in fact requires 20 amps and you have a properly wired 30 amp circuit you should be fine but plesae describe the plug and then the receptacle you have
  • Nov 1, 2010, 04:54 PM
    bsjbrown
    Comment on ballengerb1's post
    Looking at the NEMA Straight Blade Configurations chart, the receptacle is 6-20R and the plug on the unit is a 6-20P.
  • Nov 1, 2010, 05:01 PM
    stanfortyman
    Quote:

    Originally Posted by bsjbrown View Post
    the receptacle is 6-20R and the plug on the unit is a 6-20P.

    WHY do you have a 30A breaker feeding a 20A receptacle? That was wrong from the start.

    Change the breaker to 20A and plug it in.
  • Nov 1, 2010, 09:55 PM
    creahands

    The amps required by a unit, as recommended by manufacturer, should be size of breaker. If larger the unit will not be protected and if overloaded could cause a fire.

    Chuck