    200 amp service disconnect to150 amp max panel?
    There are two 200 amp service disconnects feeding two Challenger 150 amp service panels. Can you do this?
  • Oct 30, 2010, 05:59 AM
    tkrussell
    As long as the 200 amp disconnects have either 150 amp circuit breakers or fuses protecting the 150 amp panels.
  • Oct 30, 2010, 02:51 PM
    stanfortyman

    What TK said.

    My question would be WHY would you bother doing this?