  • Oct 27, 2010, 08:48 AM
    wayne306
    Why thunders tripping RCD
    Hi, can any one tells me why thunder tripping RCD, and how can I solve this problem?
    Thanks and regards Wayne
  • Oct 27, 2010, 09:27 AM
    ma0641
    Where do you live? RCD terminology is not widely used in the US. We use A GFCI which is basically the same. I don't think thunder is the problem, I think it is the lightning. You are either getting a surge or ground fault that is tripping the unit. Is it outside? Does it get wet? That's a common problem when water gets inside. Make sure that grounding is properlyconnected in the box, the unit stays dry and all ground wires in the outlet box are connected.
  • Oct 27, 2010, 09:53 AM
    tkrussell
    Yes, RCD is short for Residual Current Device, the European equivalent to the USA GFI device.

    Here is a RCD manufacturer that recognizes the issue with lightning causing nusiance tripping of RCD units.

    http://www05.abb.com/global/scot/sco...21002B0201.pdf
  • Oct 28, 2010, 07:21 AM
    wayne306
    Yes the rcd is inside in the consumer unit. Is the earth electrode which is outside but it is connected properly.
  • Oct 28, 2010, 07:55 AM
    wayne306
    By the way thanks for the pdf file it is very help full and I think that's the problem. Thanks a lot Wayne