-   -   How does 4 pole RCD operates in a unbalanced three phase system without neutral (https://www.askmehelpdesk.com/showthread.php?t=515183)

  • Oct 9, 2010, 07:20 PM
    priyantha
    How does 4 pole RCD operates in a unbalanced three phase system without neutral
  • Oct 10, 2010, 04:33 AM
    tkrussell
    The sensing coil will still monitor for any earth leakage and trip if any is seen over tolerance.

    Need to check with the manufacturer or your RCD, as many need either a neutral or earth ground on the 4th pole for the test button to operate properly.