-   -   What could cause loss of pressure (https://www.askmehelpdesk.com/showthread.php?t=515062)

  • Oct 9, 2010, 11:21 AM
    td21884
    What could cause loss of pressure
  • Oct 9, 2010, 11:23 AM
    afaroo

    Need more information, loss of pressure where? Thanks

    John
  • Oct 9, 2010, 11:26 AM
    td21884
    When the washer is filling I have no water upstairs in the kitchen or the bathroom
  • Oct 9, 2010, 11:29 AM
    speedball1

    Age of house? Material of pipes? Pump or city water? If on city water Is there a PRV, (pressure reducing valve) installed? Problem just came on all of a sudden or was it gradually? Let's have more information. Cheers, Tom
  • Oct 9, 2010, 11:32 AM
    afaroo

    Once again respond to Tom's question, Thanks.

    John
  • Oct 9, 2010, 11:32 AM
    td21884
    Comment on speedball1's post
    1970,copper,well, it has beengetting worse over about 1 year. This well is 5 years old new pump and tank at the same time
  • Oct 9, 2010, 11:35 AM
    ballengerb1

    Post just once not 3x. Pressure is likely fine but volume very low. Do you have an outside spigot, how is its flow? Done any plumbing work recently? We will have answers after we hear back from you
  • Oct 9, 2010, 11:42 AM
    td21884
    Sorry new at this. Yes out side is fine (the one closest to the well, the one one opposite side of house is weaker). No new plumbing work in about 4 years, except new field system this past June.

    When the washer is filling, I have no water upstairs in the kitchen or in the bathroom.
  • Oct 9, 2010, 12:13 PM
    ballengerb1

    Do you know how many gallons per minute your pump is producing and at what psi?
  • Oct 9, 2010, 12:47 PM
    td21884
    Comment on ballengerb1's post
    No I don't, all I know is that is a Gould 1/2 hp
  • Oct 9, 2010, 01:50 PM
    mygirlsdad77

    If you have a water softener, put it on bypass and see if the problem is still there. Also check for a water filter and change it if you have one.
  • Oct 9, 2010, 08:32 PM
    td21884
    Comment on mygirlsdad77's post
    I tried bypassing the softner, still the same. We don't have any filters.
    Thanks
  • Oct 10, 2010, 07:41 AM
    speedball1

    Bladder or pressure tank? If a bladder tank what's the charge on the bladder tank? What's then cut in and cut out limits on the control box? Any air in the lines? Any dirt in the aerator screens? Let me know, Tom
  • Oct 10, 2010, 08:36 AM
    td21884
    Bladder tank pressure is 28 psi, limit switch says 30-50. Screens at the faucets are clean.

    Also the pressure starts good at faucet then gradually drops.
  • Oct 10, 2010, 08:54 AM
    speedball1

    Quote:

    the pressure starts good at faucet then gradually drops.
    What's the pump doing during this loss? Does it kick on attempting to build the pressure back up? On the front hose bib does the pressure drop when you run it for any length of time? Back to you, Tom
  • Oct 10, 2010, 01:35 PM
    td21884
    Comment on speedball1's post
    Pump doesn't come on until the pressure gauge drops.the hose will go and neverlose pressure, does this sound like build up in the lines or possibly the pump ?
  • Oct 14, 2010, 01:55 PM
    td21884
    Comment on speedball1's post
    The hose doesn't lose pressure, no matter how long it runs, the pump will kick on when the gauge pressure drops.
  • Oct 15, 2010, 02:25 PM
    jlisenbe

    Is there a cut-off valve where the pipe enters the house?
  • Oct 16, 2010, 10:03 AM
    td21884
    Comment on jlisenbe's post
    Yes,after the bladder tank and this will shut off all.