  • Dec 31, 2006, 03:57 PM
    GoatRancher
    120V heater tape off a 240V source.
    Hi,

    My question is very similar to HandyJohn's and much my question was answered in is post. Mostly verifying my suspicion of needing a step down transformer here. Just wondering if you know of any simpler options I may be overlooking outside of running a dedicated line.

    Here's my situation:

    1) I stupidly ran 10/2 UF cable 50 feet undeground to my well house. Was in a hurry to supply water to the home. Closed things up with the backhoe. The submersible pump runs on 240V (2 hots, 1 ground, no neutral). The cable feeding to it has two hot wires (both running to the breaker) and one ground. No neutral in the cable. I should have run a fourth wire in there for neutral! Hindsight 20/20 thing here.

    2) At the moment, I'm insulating my pipes and running heater tape which takes 120V (1 green ground, 1 black hot, 1 white neutral).

    Only a couple options I see for running that heater tape:

    1) Run a 120V extension cord to it for now until figuring out what to do. Safest option that gets things functional and buys time.

    2) Off the 240V source, tap one 120V wire and the ground. Run the neutral into ground. I've heard this would complete the circuit, but I don't like doing it that way. I understand it is dangerous and not up to code. Not wise to energize a ground wire like that. I might be willing to risk it if no other options and maybe even install a seasonal switch, but that's all too Mickey Mouse. Best to go with an extension cord and later a stepdown transformer, I believe.

    ... Unless, any of you see a better idea? I'd rather not dig new trenches and run more wire right now.

    Thank you.
  • Dec 31, 2006, 04:58 PM
    Amchiller
    Quote:

    Originally Posted by GoatRancher
    Hi,

    My question is very similar to HandyJohn's and much my question was answered in is post. Mostly verifying my suspicion of needing a step down transformer here. Just wondering if you know of any simpler options I may be overlooking outside of running a dedicated line.

    Here's my situation:

    1) I stupidly ran 10/2 UF cable 50 feet undeground to my well house. Was in a hurry to supply water to the home. Closed things up with the backhoe. The submersible pump runs on 240V (2 hots, 1 ground, no neutral). The cable feeding to it has two hot wires (both running to the breaker) and one ground. No neutral in the cable. I should have run a fourth wire in there for neutral!! Hindsight 20/20 thing here.

    2) At the moment, I'm insulating my pipes and running heater tape which takes 120V (1 green ground, 1 black hot, 1 white neutral).

    Only a couple options I see for running that heater tape:

    1) Run a 120V extension cord to it for now until figuring out what to do. Safest option that gets things functional and buys time.

    2) Off the 240V source, tap one 120V wire and the ground. Run the neutral into ground. I've heard this would complete the circuit, but I don't like doing it that way. I understand it is dangerous and not up to code. Not wise to energize a ground wire like that. I might be willing to risk it if no other options and maybe even install a seasonal switch, but that's all too Mickey Mouse. Best to go with an extension cord and later a stepdown transformer, I believe.

    ....Unless, any of you see a better idea? I'd rather not dig new trenches and run more wire right now.

    Thank you.

    I thimk the obvious solution is to use a 220 volt heat tape! Available at any supply house. I buy it in 250 ft. rolls for commercial use. If you need a long distance pipewrapped, it is worth considering. Grainger has it also.
  • Dec 31, 2006, 05:34 PM
    tkrussell
    Compare the cost of a transformer,sized 125% larger than the load of the 120 volt heat tape you already have against purchasing the amount of 240 volt tape you can use to eliminate the need for a transformer.

    In any case, the load of the heat tape and the motor should not exceed 24 amps, assuming you have a 30 amp breaker on the #10-2 cable.
  • Jan 1, 2007, 12:55 PM
    GoatRancher
    Thank you to you both! This is really a great website!

    I never even thought of going with alternate heat tape. Just like that 220V well shed light bulb that was suggested to HandyJohn. Great idea. Thank you.

    Too late now, however. I already installed the 120V tape and it works just fine. Would be much hassle and time lost to redo it. Might as well go with a transformer and have access to 120V out there.

    I thank you again for this useful information all the same and information on selection of a transformer. Much appreciated.

  • All times are GMT -7. The time now is 10:04 PM.