    I have 1000 feet to go from my electrical supply to my well, I was planning on going with 120/240 wire buired in a trench 18" deep. The other end will have a well pump rated at 2K watts, plus some ligths, etc. I was figuring no more than 20 amps. So the question is, what is better, least cost ?

    1. run 8-3 UF direct burial cable ?
    Or
    2. 3/4 pvc sch 40 pipe with four individual 8 gauge wires inside ?

    Or something else ?
  • Oct 4, 2010, 03:40 PM
    stanfortyman

    Wow! 1000 feet?? WHY so far?


    Anyway, figuring a load of 16A, @ 240v (the 120v stuff will be incidental) you are going to need #2cu. I would run this in conduit definitely.
    A load of 10A would require on #4cu.