    Replaced fuse box with breaker panel - problem (some circuits reading 220 volts)
  • Sep 27, 2010, 06:49 PM
    stanfortyman

    Who replaced the panel?
    What circuits are reading 240v?

    Can you please use a few more words to describe your problem? The way it is written it is impossible to figure out.
  • Sep 27, 2010, 07:28 PM
    ballengerb1

    Who did the actual work and installed the braekers and the wire? Most homes with 240 vac coming in might welll expect some 240 vac circuits like for HVAC.
  • Sep 28, 2010, 08:01 AM
    Stratmando

    I see some electricians not make enough notes when changing panels, such as Low voltage ac wiring which is usuall a no brainer as many run with the supply wiring.
    The phase circuits are on in multicircuits.
    Sometime a white and black mabye on a 240 volt breaker, but when reconnecting, they may put the white on a neutral bar.
    Or viceversa.
    If the hot and neutral that supply a pane are reversed, you will get 240 volts on every other circuit.
    How many circuits is this affecting?