  • Sep 22, 2010, 12:16 PM
    canoehead2
    I 'm installing #2-4 alum wire through crawl space
    I need to know if #2-4 alum wire needs to be put in conduit if it travel under a house in a crawl space some of which is exposed , the house sits on piers.
  • Sep 22, 2010, 12:23 PM
    smoothy

    Don't know if code requires it but I think it's a good idea, Certain animals appear attracted to electrical fields and would chew on the wires.

    I wired my shed using armoured cable just because of that.
  • Sep 22, 2010, 12:31 PM
    canoehead2

    Thank you:) smoothy I'am confused I wouldn't think anyone from northern Virginia would have shermans picture up
  • Sep 22, 2010, 12:36 PM
    donf

    Can you please tell me what #2-4 cable is?

    Could you possibly mean that you are planning on using four(4) #2 conductors?

    #2 AL conductors can only handle 100 Amps, if it is used as a main service feeder (see T.310.15(B)(6)). T.310(16) gives you 75Amps (if used any where else) in the 60c column.
  • Sep 22, 2010, 12:46 PM
    canoehead2

    4 wires of # 2 alum. To feed 100 amp sub panel with 100 breakers on both sides, this all comes from a 200 amp main panel in main house , I am putting on an addition that does not have an enclosed crawl space yet but will next spring
  • Sep 22, 2010, 02:16 PM
    tkrussell
    Must be installed in conduit.