  • Dec 27, 2006, 09:23 PM
    rockstar304
    Furnace will not light.
    Hello to all.

    Have a 35 yr old furnace that was never a prob till this yr.

    Pilot lights and stays lit
    Thermostats good[both] call for heat
    When they call for heat the relay on the aquastat kicks in and the teco pump[replaced 5 yrs ago] starts to turn

    Water temp is always at zero aquastate not turning on the gas?This is the main problem

    Furnace periodically tries to start but there is only avery small flash[really nothing] near the pilot light

    Link to a pic of the[aquastat.

    http://i114.photobucket.com/albums/n...04/pic0017.jpg

    On the left is the relay that has 2 sets of contacts above that is the themostat connections

    In the middle is the temp set and section that senses heat.

    On the right another relay I thinK and some electrical connections.

    Have taped on the gas valve and whatnot.played with the temp setting too retightened electrical connections.

    Need to get that water to heat up--it is going to get chilly tomorrow. Does not light even manually--there is a switch n top of the controller auto and manual--both seem to work the same. Both manual and auto kick in the relay, but no heat just the pump.

    Thanks.
  • Dec 30, 2006, 08:15 AM
    mustang11
    Quote:

    Originally Posted by rockstar304
    hello to all.

    have a 35 yr old furnace that was never a prob till this yr.

    Pilot lights and stays lit
    thermostats good[both] call for heat
    when they call for heat the relay on the aquastat kicks in and the teco pump[replaced 5 yrs ago] starts to turn

    water temp is always at zero aquastate not turning on the gas?This is the main problem

    furnace periodically tries to start but there is only avery small flash[really nothing] near the pilot light

    link to a pic of the[aquastat.

    http://i114.photobucket.com/albums/n...04/pic0017.jpg

    on the left is the relay that has 2 sets of contacts above that is the themostat connections

    in the middle is the temp set and section that senses heat.

    on the right another relay I thinK and some electrical connections.

    Have taped on the gas valve and whatnot.played with the temp setting too retightened electrical connections.

    Need to get that water to heat up--it is gonna get chilly tomorrow. Does not light even manually--there is a switch n top of the controller auto and manual--both seem to work the same. both manual and auto kick in the relay, but no heat just the pump.

    Thanks.

    Sometimes all 5 burners will light and furnace will come on sometimes all burners won't light light causing heat to fail
  • Dec 30, 2006, 08:45 AM
    rockstar304
    Thanks Mustang11. It was the thermopile [not thermocouple,but function is the same] that was going fast. It was the original one anda real pain to get out,and getting the new one in was more of a pain. Very close tolerances. The pilot lit and stayed on, but when the 5 burners were meant to come on the gas valve was not open. Replaces it for$30.00 and all seems to be working fine.

    Thanks again.