Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Will a 10 amp 220 v UPS be sufficient to power a computerised sewing machine (https://www.askmehelpdesk.com/showthread.php?t=504094)

  • Sep 2, 2010, 05:30 AM
    dihil
    Will a 10 amp 220 v UPS be sufficient to power a computerised sewing machine
    My wife has a computerised sewing machine will a 220v 10amp UPS be sufficient to power this machine.
  • Sep 2, 2010, 06:47 AM
    smoothy

    What are the current requirements and ratings of the Sewing machine.
  • Sep 2, 2010, 07:44 AM
    creahands

    If there is no label on machine with rating needs,contact manufacturer with model # and they can help u.

    If u have manual, info should be in it.

    Chuck
  • Sep 2, 2010, 03:13 PM
    donf

    Where are you located? Most U.S. home sewing machines are 120VAC, not 240.
  • Sep 4, 2010, 03:28 AM
    dihil
    Quote:

    Originally Posted by smoothy View Post
    What are the current requirements and ratings of the Sewing machine.

    The machine is 220 - 240v and 45w
  • Sep 4, 2010, 03:45 AM
    tkrussell
    UPS units can be the minimum size of 125% of the load to be served to achieve the minimum runtime.

    You stated the unit draws 10 amps at 220 volts, that equals 2200 watts.

    What is 45 watt?

    You do realize the during a power failure, the UPS will be running on battery, and will run out of power in time. Time will be inversely proportional to load.

    To increase runtime, you can get a larger wattage unit.
  • Sep 6, 2010, 10:41 PM
    dihil

    Hi tkrussell
    The sewing machine is 45w and the UPS output is 10amps at 220v
  • Sep 7, 2010, 04:25 AM
    tkrussell
    Then the 2200 watt UPS should run a good long time with only a 45 watt load during a power failure.