  • Aug 17, 2010, 12:04 PM
    mcm818
    Low voltage splices require a j-box
    Hi.

    I am renovating and am installing a few low voltage lights.

    Under the 2008 NEC, do the splices need to be in j-boxes?

    Also, the splice is aluminum to copper. Am I required to use the purple, liquid filled, expensive nuts on the splices or will normal wire nuts pass code?

    Thanks so much.


    Mark from NJ
  • Aug 17, 2010, 12:20 PM
    mcm818

    Also, as to the Ideal purple nuts, I have read that they have failed in field tests, but am not sure if the fact that this is a low voltage situation makes failure less likely. If these nuts are a problem, how do I protect my splices?

    Thanks in advance for your help.
  • Aug 17, 2010, 01:14 PM
    tkrussell
    Low voltage splices in the ground can be anywhere underground. A wise installer would use some sort of hand hole for later access.

    The purple wirenuts are for aluminum to copper splices, but I have no experience with those. I don't get much small wires to worry about.

    These wire nuts are not rated for direct burial.

    I would use a crimp butt splice that is AL-CU rated and cover with heat shrink.
  • Aug 17, 2010, 03:08 PM
    mcm818
    Many thanks.
  • Aug 17, 2010, 03:46 PM
    mcm818

    One issue, though... these are not going underground. They are downlights being placed in an eave. Does this make a difference?

    Thanks.
  • Aug 18, 2010, 02:20 AM
    tkrussell
    No difference.