Forgive me if Ive ask this question before, I think I wrote it out, but had to leave and I just closed it rather than posted.
Two years ago when I had my 15KW electric furnace installed, I noticed that when ever it would run, it would make the lights dim, and they wouldn't get bright again until it cut off. The same goes for fans, you can hear fans slow down (such as the bathroom fan, and the fan by my bed)
Now I had one problem where I was tripping the breaker for my furnace, as the unit was under warranty, I just let them deal with it, turns out my furnace is drawing about 46 AMPS (if memory serves) and they wired it to a 50 AMP breaker, as the wire was already rated for 60 AMPs, they just swapped the breaker and I haven't had a problem since.
The man did tell me that my voltage at the box was to low, which was causing the furnace to draw excessive amps. I remember his reading at the lugs were about 232 volts. He said I needed to call the power company and tell them to check the transmormer. So I did, they came out and checked it and said everything was okay, so I didn't worry about it anymore.
About 6 months ago, I noticed they changed our transformer. This was during the summer, so I didn't see what difference it made on my lights dimming. Well, now that we are in the heating season, there is no change in my dimming problem or fans slowing down.
It should also be noted that I share a transformer with a neighbor.
Now last night, I got into a conversation with an electrician who said that my low voltage needs to be fixed, this can ruin my elements and burn up the motors in my fans. It also drawing excessive current and consuming extra electricity. I agree'd.
Well that is, until I got home, and for the first time since the new transformer was installed, actually tested my voltage. Turns out that now at the 240 AC receptacle I now have about 250 volts!
So my question is, if Im getting 250 volts, why are my lights and fans still slowing down? And will this hurt them/shorten their life?
The stats of the electric system are as follows:
I have one 200 AMP murray box in the basement. Its about 200 feet from the transformer. The house is 60 years old, so Im sure this box is an upgrade. At my AC outlet there is 250 volts. The furnace is 15KW, split between two breakers, one 60 and one 30 AMP.
What is the solution for this? This can't be normal. I have been in so many huge kitchens with 100 AMP electric fryers, ovens, etc, and their lights don't dim while they are cooking...