  • Jul 21, 2010, 09:08 PM
    Dana6
    Troubleshooting my a/c unit
    I have a Rudd unit. The condenser is outside and the unit is in the basement. It is a dual heat/air unit. Upon returning home this afternoon, I noticed it was hot inside the house. Changing the thermostat setting didn't help kick the unit on. I flipped the breaker, the unit acted like it was going to fire up, and quickly stopped. I changed the thermostat out, but that didn't help. When I turn the breaker switch on, the condenser fan runs, but the motor doesn't fire up. What could the problem be? Please help... I have six children and it is quite unbearable to them inside. Thank you!
  • Jul 22, 2010, 07:19 AM
    hvac1000

    Check to be sure the contactor in the outdoor unit is pulling in. Then check power wires going to the compressor. Then test/check the compressor capacitor. If all else fails call for service.
  • Jul 22, 2010, 10:36 AM
    wmproop

    Quote: the condenser fan runs, but the motor doesn't fire up.
    Are you talking about the blower motor in the furnace/airhandler?or outside not running

  • All times are GMT -7. The time now is 05:43 PM.