-   -   30 amp double breaker so do I need 10/2 or 10/3 for an air conditioner? (https://www.askmehelpdesk.com/showthread.php?t=489465)

  • Jul 18, 2010, 12:16 PM
    errtra
    30 amp double breaker so do I need 10/2 or 10/3 for an air conditioner?
    I plan to run a 12 foot dedicated line to a 240 service box for an AC that is 230/208, install a 30amp double breaker, I assume #10 wire, but 10/2 or 10/3?
  • Jul 18, 2010, 03:04 PM
    hvac1000
    Quote:

    Originally Posted by errtra View Post
    I plan to run a 12 foot dedicated line to a 240 service box for an AC that is 230/208, install a 30amp double breaker, I assume #10 wire, but 10/2 or 10/3?

    It all depends upon what the A/C unit says it needs for protection. It could be a 25 amp breaker. Always read the directions that are on the unit or on the install sheet. To large a breaker can eventually damage the unit since the protection rate will be to high. Number 10 will take 30 amps and you will need two power wires and a ground for 3 wires in total.
  • Jul 18, 2010, 05:48 PM
    errtra
    Thanks - I receive the unit tomorrow but any online manuals, etc. for it do not seem to indicate anything about the wiring, etc. but perhaps when I get it it will say something,